How many negative air machines are needed for an 80' x 40' x 20' room if the effective capacity of one machine is 1,600 cfm?

Prepare for the Asbestos Abatement Supervisor Test. Use flashcards and multiple choice questions with hints and explanations to ace your exam!

To determine the number of negative air machines required for an 80' x 40' x 20' room, we first need to calculate the room's volume in cubic feet. The volume is found by multiplying the length, width, and height of the room:

Volume = Length x Width x Height

Volume = 80 ft x 40 ft x 20 ft

Volume = 64,000 cubic feet

Next, we need to assess the air exchange requirement. For asbestos abatement projects, a common standard is to achieve a minimum of 4 air changes per hour (ACH). To do this, we need to know how much air must be moved in a given hour.

  1. Calculate the total air volume needed per hour:

Required airflow (in cubic feet per hour) = Volume x ACH

Required airflow = 64,000 cubic feet x 4 ACH = 256,000 cubic feet per hour.

  1. Convert the effective capacity of one negative air machine from cubic feet per minute (cfm) to cubic feet per hour:

One machine capacity = 1,600 cfm

Convert to hourly: 1,600 cfm x 60 min/hour = 96,000 cubic feet